I'm building a small cabin in North Queensland and have an oven and cooktop to join and then out to the switchboard
Appliances:
Devanti induction cooktop, model CT-IN-C-YL-ID3501: 220-240V, 3000-3800W, double-square (Class II) symbol on the label
Sölt 60cm built-in oven, model GGSO605MS: 2.1kW. Has a wall mounted lead will need to cut.
Existing wiring
One cable from the wall to the switchboard, printed "Prysmian 450/750V V-90/3V-90, 2C x 6mm² + E 2.5mm² Cu"
Cores are red, black and green
Switchboard
The main breaker is a Hager MSN132, which I believe is a 1-pole 32A C-curve MCB. I have a second identical 32a breaker for the oven and cooktop
My rough numbers
Cooktop at full power: about 15.8A. Oven: about 8.8A. Together: about 24.6A
My plan:
Hager 32a breaker for the board (photo)
A junction box for the joins. I have 500V/40A containing 4 X screw tee connectors marked "3x6mm / 4x2.5mm".
My questions for the sparkies here:
- Are the junction box and connectors sufficient?
- Is the 32A Hager right for this circuit on 6mm² TPS, given a 3.8kW cooktop and 2.1kW oven?
- My main is also 32A. Is a cabin with a 32A main realistically able to run induction and an oven plus everything else?
- The oven and wall wiring have three cables, the cooktop just two. Is this okay to all go through the same connectors? I.e. 3 in +/- (oven, cooktop, wall wires), 2 in earth (just oven and wall wires)
- Are the tee connectors in the 40A box acceptable if they carry their own rating and compliance marking? Does mixing 6mm² and thin appliance leads in one grub screw worry you?