Disclaimer, I asked Claude to summarise all my troubleshooting I've done with it rather than write from scratch.
My parents’ system (UK), installed under a year ago:
Solis S5-EH1P3.6K-L hybrid inverter
1× Duracell Dura5 (5.12kWh, 48V LFP), CAN comms
What happened
15 Nov: grid outages logged at 02:45, 08:34 and 15:09.
From 15:09, the inverter has shown NO-Battery, plus CAN_Comm-FAIL around restarts.
Since then the battery won’t charge or discharge.
Current state (AC on)
Info page 1: battery voltage 0.4V, charge power 0.00kW.
Info page 2: Device Status “Waiting”, Battery Status “NO-Battery”, Grid Normal.
BMS page: 52.68V, 0.3A, SOC 66%, SOH 100%, BMS Status Normal, charge limit 40A, discharge limit 100A.
Home screen shows “CAN OK”.
Battery: 125A DC breaker on, LED flashing green, no alarm light.
SolisCloud: inverter shows “Info”, battery shows “Offline”.
Multimeter
52V DC at the battery terminals.
52V DC at the inverter end of the battery cables, disconnected from the inverter.
The odd bit
With the grid connected, switching the battery off killed the inverter completely: screen, LEDs and datalogger all went dead.
With the AC isolated, switching the battery on boots the inverter and it runs from the battery. The BMS shows about 0.3A going out.
Throughout, the inverter still reads 0.4V on its battery input.
So the battery and cables deliver 52V and are powering the inverter, while the inverter measures no battery voltage.
Tried so far
Cycled the battery breaker.
Full cold restart: AC and battery off for 5+ minutes, then battery on first, then AC.
Manual battery wake-up from the inverter menu.
None of it changed anything.
Installer’s view
They checked remotely and say the battery is at fault. Given the readings above, I think it’s the inverter’s battery input (a fuse, relay or measurement circuit), damaged by the outage.
Questions
Has anyone seen this failure on a Solis hybrid? What was the fix?
Is there anything internal that’s known to fail like this, such as a battery input fuse?
Any tips for getting the installer or Solis to accept it’s an inverter warranty issue?
Anything else worth trying in the meantime?