r/diySolar • • Feb 10 '23

DIY AC

Thumbnail
youtube.com
23 Upvotes

r/diySolar • • 6h ago

Misc Safety warning: Anker SOLIX Backup Auto-Switch creates a floating neutral (IT-grid) without a PE-N bond

Post image
7 Upvotes

I’ve been looking closely at the product page and installation instructions for the Anker SOLIX Backup Auto-Switch (63A, 1-phase), and there is a major electrical safety issue that Anker completely fails to mention in their marketing.

On their European product pages, Anker claims you can simply install this switch behind your main breaker using "just two cables" to get whole-home backup power. If an installer or DIYer actually wires it strictly according to Anker's simplified instructions, it creates a hazardous situation.

Here is what actually happens when the grid goes down:

  1. No automatic PE-N bond (Floating Neutral): When the Auto-Switch disconnects the house from the public grid (2-pole disconnect of L and N), the neutral (N) is completely isolated from the utility's transformer ground. Because neither the Solarbank Max nor the Backup Auto-Switch has a built-in grounding relay to bond Neutral to Protective Earth (PE) during island mode, your home shifts into an ungrounded IT-grid with a floating neutral.
  2. RCDs (Earth Leakage Breakers) stop working: Without a PE-N bond in island mode, there is no return path to the inverter for fault currents. Standard 30mA RCDs (GFCI/aardlekschakelaars) in your consumer unit will not trip if someone touches a live wire or if an appliance develops a ground fault. Furthermore, sensitive appliances like modern gas boilers (with ionization flame sensors) will often throw an error or refuse to run on a floating neutral.
  3. Missing local ground electrode requirement: For homes with a standard TN-S or TN-C-S grid connection (where earth is supplied by the utility company), switching to island mode under European electrical codes (IEC 60364 / NEN 1010) requires a local earth rod with a sufficiently low resistance, paired with an external relay that automatically bonds N to PE only when off-grid. Anker mentions none of this—only a vague one-liner that the unit "must be properly grounded."

Conclusion:
Unlike proper hybrid inverters (which include an internal N-PE grounding relay that engages during off-grid operation), the Anker Backup Auto-Switch is just a basic transfer switch with a built-in CT meter. Selling this as a plug-and-play "whole-home backup solution" without warning installers about external N-PE bonding and local earthing requirements is misleading and unsafe.

I have already reported this directly to Anker's support/compliance team. Curious to hear if anyone here has installed one and how your electrician handled the N-PE bonding during island mode!


r/diySolar • • 1h ago

4000 LFP cells for $8200. $100/kwh

Thumbnail gallery
2 Upvotes

r/diySolar • • 1h ago

Extension Cords to Loads

Thumbnail reddit.com
1 Upvotes

r/diySolar • • 2h ago

a system to charge a 69kwh car battery

0 Upvotes

Guys I am a total noob in this. I have an EV and I am wondering how possible is to charge the EV using solar energy. I only use the car in weekends so that there is a lot of time to charge the car midweek. do you think a setup like this is doable? would it be worth to do this system as full of grid or hybrid?

since the size of the battery car is big, I am having a hard time understanding how the solar energy can be managed so that it can charge the car, for example in an off grid system.

I am inclined for an off grid system so it can be as independent and autonomous as possible.


r/diySolar • • 20h ago

At last, I hold the power of the sun!

Thumbnail gallery
21 Upvotes

It lives!

560 AH Ecoworthy LifePO4
950 Watts Solar

As compact as possible. Minimal wire. Straight copper bar on P+.
Total cost (including panels and brackets): $3,646.14

... and now I just have to finish the rest of the bus...


r/diySolar • • 4h ago

Battery Back + Duel Fuel Generator

Thumbnail reddit.com
1 Upvotes

r/diySolar • • 3h ago

Question Good deal on panels ?

0 Upvotes

I have the opportunity to purchase 16 455W panels for $2,160. This would be a DIY setup. Is it prudent to go ahead and purchase these panels before December? Is this a good price?
Thanks.


r/diySolar • • 9h ago

Question 8K-SG01LP1-US + 15KW-SG01LP2-US-AM3 sharing same battery bank

Thumbnail reddit.com
1 Upvotes

r/diySolar • • 12h ago

What can you run for appliances using off grid solar?

Thumbnail reddit.com
1 Upvotes

r/diySolar • • 18h ago

hooking up 3 panels.

Thumbnail reddit.com
1 Upvotes

I bought several small solar panels from TEMU, two are listed at 15w the other one says it's 1,000 watt but it's not that much larger than the others reviews say that it can't produce more than about 22 Watts.

are these any good at all for charging phones etc?

can these be hooked together to go into a controller? The large one came with a little controller that appears to have USB outputs, how do I connect the panels? series? parallel?

any help is much appreciated


r/diySolar • • 20h ago

Judy Power box solar charging .. help?!!

Thumbnail reddit.com
1 Upvotes

r/diySolar • • 1d ago

Question 4S2P or 2P4S - did I choose the wrong setup?

Post image
7 Upvotes

I recently bought 8 litime 12v100ah batteries and put them together in a 4S2P setup.

But I've seen some people say it's better to connect batteries in parallel first, then in series.

Now I'm wondering if I should have gone with that approach instead. Does it actually make a difference?

What would you guys recommend?


r/diySolar • • 22h ago

Expected output from 2 solar panels

Thumbnail reddit.com
1 Upvotes

r/diySolar • • 22h ago

An okay solar generator setup?

Thumbnail
reddit.com
0 Upvotes

r/diySolar • • 1d ago

Question A solar company left their trash after installation, are they worth keeping?

Post image
14 Upvotes

It looks like cables for batteries and a few breakers not sure if it’s worth anything


r/diySolar • • 22h ago

Question Hive mind... should I repair or not

Thumbnail reddit.com
1 Upvotes

r/diySolar • • 17h ago

Would this work?

Post image
0 Upvotes

r/diySolar • • 1d ago

Plug in/balcony solar and utility charges for excess solar

Thumbnail reddit.com
1 Upvotes

r/diySolar • • 1d ago

UL Listing for panels, batteries , and inverters for a non exporting residential solar setup?

Thumbnail reddit.com
1 Upvotes

r/diySolar • • 18h ago

Question Has anyone here ever had to.... From Homeless, Built solar off scraps ?

0 Upvotes

Sorry, that was rude. From a $100 budget.. What do You understand? If we can get past the Sun is real... I would like to have a conversation. I've done it, I could do it 12 years ago. At a campground.

So I'm interested in what y'all consider diy ??


r/diySolar • • 1d ago

Question Can a 3-pin socket be added to a house battery/inverter to be used separately from the mains?

Thumbnail reddit.com
0 Upvotes

r/diySolar • • 1d ago

Any thoughts? Thank you!

Thumbnail gallery
0 Upvotes

r/diySolar • • 1d ago

Mounting panels directly on wood?

Post image
0 Upvotes

Hi,

I'm making a solar mount and want to know whether I can skip buying aluminum rails or unistrut. Seems like a waste.

I'm using 2x8 wood with blocking plates. Why wouldn't I be able to use the mounting holes on the rear of the panel with something like an L bracket? or is there a better way?

Thank you.