I’ve been looking closely at the product page and installation instructions for the Anker SOLIX Backup Auto-Switch (63A, 1-phase), and there is a major electrical safety issue that Anker completely fails to mention in their marketing.
On their European product pages, Anker claims you can simply install this switch behind your main breaker using "just two cables" to get whole-home backup power. If an installer or DIYer actually wires it strictly according to Anker's simplified instructions, it creates a hazardous situation.
Here is what actually happens when the grid goes down:
- No automatic PE-N bond (Floating Neutral): When the Auto-Switch disconnects the house from the public grid (2-pole disconnect of L and N), the neutral (N) is completely isolated from the utility's transformer ground. Because neither the Solarbank Max nor the Backup Auto-Switch has a built-in grounding relay to bond Neutral to Protective Earth (PE) during island mode, your home shifts into an ungrounded IT-grid with a floating neutral.
- RCDs (Earth Leakage Breakers) stop working: Without a PE-N bond in island mode, there is no return path to the inverter for fault currents. Standard 30mA RCDs (GFCI/aardlekschakelaars) in your consumer unit will not trip if someone touches a live wire or if an appliance develops a ground fault. Furthermore, sensitive appliances like modern gas boilers (with ionization flame sensors) will often throw an error or refuse to run on a floating neutral.
- Missing local ground electrode requirement: For homes with a standard TN-S or TN-C-S grid connection (where earth is supplied by the utility company), switching to island mode under European electrical codes (IEC 60364 / NEN 1010) requires a local earth rod with a sufficiently low resistance, paired with an external relay that automatically bonds N to PE only when off-grid. Anker mentions none of this—only a vague one-liner that the unit "must be properly grounded."
Conclusion:
Unlike proper hybrid inverters (which include an internal N-PE grounding relay that engages during off-grid operation), the Anker Backup Auto-Switch is just a basic transfer switch with a built-in CT meter. Selling this as a plug-and-play "whole-home backup solution" without warning installers about external N-PE bonding and local earthing requirements is misleading and unsafe.
I have already reported this directly to Anker's support/compliance team. Curious to hear if anyone here has installed one and how your electrician handled the N-PE bonding during island mode!