I put together a single-file 3D + 2D hydronic simulator (Three.js + 2D Canvas P&ID) using Gemini Argon to help visualize primary-secondary decoupling and low-loss header regimes for junior engineers and students.
**What is modeled and analyzed:**
- **Direct-Coupled Pump Conflict (No Separator):** A primary boiler loop (DN65) tied directly to 3 secondary zone pumps with different shutoff heads: Z1 Panel Radiators (55 kPa), Z2 AHU Heating Coil (110 kPa), and Z3 Underfloor/FCU loop (38 kPa). When primary flow lags and Z2 ramps up, manifold pressure drops to `-30.7 kPa`, starving Z1 to `56%` and pulling `-0.68 m³/h` backwards through Z3 (with a toggleable non-return check valve on Z3).
- **Caleffi 3D / 10D Sizing Rule:** Adjustable `DN50–DN100` headers and `1.5D–4.0D` separator body ratios showing internal velocity (`v = Q/A = 0.100 m/s` at `3.0D` vs `≤ 0.15 m/s` threshold), air microbubble venting, and dirt separation efficiency.
- **Coupled Enthalpy Balance across the 3 Separator Regimes:**
- `Qp = Qs` (`12.0 m³/h`): `70.0 °C` supply / `52.5 °C` return (`< 54 °C` flue dew point → condensing active at `91.0%`).
- `Qp > Qs` (`13.8 > 6.95 m³/h`): Hot downward bypass mixes `70 °C` supply into `46.4 °C` building return, raising boiler return to `58.1 °C` and killing condensation.
- `Qp < Qs` (`7.2 < 13.45 m³/h`): Upward return recirculation blends secondary supply down from `70.0 °C` to `58.9 °C`.
Live browser simulator (single HTML file, no install):
https://www.meptasarim.com/hydraulic-separator-simulator.html
*Disclaimer: Informational & educational model only — not for engineering design.*
For those of you commissioning condensing boiler plants: how often do you still find constant-speed primary pumps running in Regime 2 (`Qp > Qs`) and preventing the boilers from ever condensing?